Dear New_Bird, I'm going to try to answer.
I suppose you have CP342-5 as master , so you use GSD file for EM277. When you insert an EM277, you will have to insert Inputs and Outputs. I suggest you insert an 'Universal module'. Double click on it and you can insert In- and Outputs (20 word in and 20 word out)
This is the location where you store data from S7-200
Pleas have a look at following faq: http://support.automation.siemens.com/WW/view/en/18208090 See point 5 Best regards, Wizard |