3/18/2020 12:41 PM | |
Joined: 12/19/2014 Last visit: 4/24/2024 Posts: 5 Rating: (0) |
Hello Experts, I am facing a problem with 1212C DC/DC/DC(6ES7212-1AE40-0XB0, FW 4.1)and CM1241(241-1CH32-0XB0, FW 2.1 ) with Siemens MAG 8000 flowmeter. The problem is that the flow rate in Flow meter display is fluctuating at zero flow(means no physical flow). this fluctuation further affecting Totalizer value of Flow meter.
Please suggest anything to check .... ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/18/2020 12:50:12New subject after splitting |
|
3/19/2020 1:22 AM | |
Joined: 3/28/2010 Last visit: 5/14/2024 Posts: 1031 Rating: (211)
|
Since your post was split from a thread with RS-232, I can only assume that you are using the RS-232 interface, but the catalog sheet for the 6ES7241-1CH32-0XB0 comm module says that the module is an RS-422 interface, not RS-232. 1. The magmeter has a low flow cut-off parameter where flow rates below a cut-off value are represented as zero flow rate. See the attachment for details. 2. The other solution is to use an isolator so eliminate the ground loop. However, with RS-232 on one side and RS-422 on the other side, it's an issue to find an isolator. |
3/19/2020 6:21 AM | |
Joined: 3/28/2010 Last visit: 5/14/2024 Posts: 1031 Rating: (211)
|
There are lots of RS-485 isolators in the market. |