Hi, To check the size of the program for memory card use, you should highlight the PLC station in the project tree the go to Tools>Resources. A screen will popup showing the size of program in load memory and work memory. Load memory is where you download to from Step 7 Basic. This can be the internal flash area of the CPU OR the Simatic MC (when Simatic MC is set up for Program Mode). If the Simatic MC is set to Program mode, it must remain in the CPU as it becomes the load memory and replaces the internal flash. If the card is set to Transfer mode, the contents of the Simatic MC are copied to the internal load memory. This means that the Simatic MC can then be removed. It seems that you will require a Transfer card. The 24Mb Simatic MC would be required to perform a firmware update at this time. The HMI application is downloaded to the HMI and resides on its own internal flash. [schnippschnapp] Please see section 3.4 of the system manual. It describes how to handle Simatic MC's. I hope this helps, System Manual for S7-1200 is here: http://support.automation.siemens.com/WW/view/en/36932465 |