4/3/2021 10:45 PM | |
Posts: 3 Rating: (0) |
Here's a typical case with assumed dimensions for a pipe mounted device. The calculations are only as good as your numbers, and details of the flow conditions, but the case you've mentioned is not overly high risk.. AttachmentWellStr150mm.pdf (317 Downloads) |
This contribution was helpful to1 thankful Users |
4/5/2021 5:32 PM | |
Posts: 3 Rating: (0) |
You bet, thermowells are far more than a challenge at times. The following dimensional summary involving failures, flow tests, and a peronal experience. It may be of interest for your current selection methods. They can be addressed reliably but only with revised standards at some point. added: Thermowell dimension in cm's. Cases 1 Power plant application (published record 1981) Cases 2,3 Power plant applications (published record 1989) Cases 4,5 Flow Test (publically available 2017) Case 6 Plant Experience (personal) where a flow meter was being upgraded AttachmentCaseStudyExamples.pdf (287 Downloads) |
Last edited by: DaveBartran at: 04/06/2021 05:09:35 |
|
This contribution was helpful to1 thankful Users |