11/6/2013 4:32 PM | |
Joined: 4/24/2006 Last visit: 12/1/2023 Posts: 8596 Rating:
|
Hello, Try to use PIW752 and PQW752 Best regards, Wizard |
11/6/2013 5:16 PM | |
Joined: 4/22/2010 Last visit: 12/15/2022 Posts: 5697 Rating:
|
Hello, To be precise that's in TIA %IW752:P and %QW752:P The reason for the need of using PER inputs/outputs is described here: Where and when do you need peripheral addressing? Regards, Marcjan |
Last edited by: Marcjan at: 11/6/2013 5:17 PMProblem solved? |
|
This contribution was helpful to
1 thankful Users |
11/26/2013 11:54 AM | |
Joined: 10/10/2005 Last visit: 11/27/2023 Posts: 1916 Rating:
|
Hello, see the example/description of the FAQ: http://support.automation.siemens.com/WW/view/de/77316903 With best regards |