Hello Jeebs, in general I would not log directly to an archive in the network, because you have no logs when it is disconnected for any reason. Better create the logs on a local memory and copy resp. move them to the network when they are closed - see How do you safely copy and move archives with WinCC Comfort/WinCC Advanced? Anyway, logs have the property "Restart behaviour > Enable logging at runtime start". Deactivate it and e.g. check the point of runtime start in the PLC and set a tag after the required delay. On change of this tag call system function StartLogging. Regards, Frink |