9/2/2013 9:27 PM | |
Joined: 5/22/2012 Last visit: 3/24/2022 Posts: 895 Rating: (67) |
Hello, |
Last edited by: O_Moderator at: 9/4/2013 2:31 PMLast edited by: zako_ at: 9/2/2013 9:28 PM |
|
3/10/2014 2:32 PM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hello, this bit must send from the PLC trough PROFIBUS to the drive. Regards Christoph |
3/11/2014 9:30 AM | |
Joined: 10/11/2006 Last visit: 5/27/2024 Posts: 5853 Rating: (793)
|
Hello, here is an example with telegramm 354. You can change to "Standard telegram 999 (extended)". Then you can change telegramm parameters. If you need additional data`s you can change this under "Actual value" --> Extension. So you can add additional data`s for p1138 and p1139. AttachmentD:\temp\G120C_TelegramExtension.pdf (1395 Downloads) |
Last edited by: TechTeam at: 3/11/2014 9:31 AMWith best regards, |
|
This contribution was helpful to1 thankful Users |
3/11/2014 12:53 PM | |
Joined: 5/28/2013 Last visit: 2/1/2023 Posts: 112 Rating: (3) |
Thanks for the tip, but i couldn't find the first screen to "Display extended parameters" is it in TIA? |
3/11/2014 3:20 PM | |
Joined: 5/28/2013 Last visit: 2/1/2023 Posts: 112 Rating: (3) |
Ops, forgot the attachment for checking the address... |
3/12/2014 2:00 PM | |
Joined: 5/28/2013 Last visit: 2/1/2023 Posts: 112 Rating: (3) |
It worked, thanks all for support. |