Hi, As from TIA V15 it is possible to display the “initial value” that triggers supervision (S7-Graph and S7-ProDiag supervisions on the HMI), that means it is possible to identify which was the cause that triggers a ProDiag supervision. In the PLC Code Viewer object there is an additional button that toggles between the actual value monitoring and the “prints screen” in the moment of the fault trigger. The relevant contacts to the trip are marked in red. The alarm shows also the tag that trigger the alarm. A new object (Criteria Analysis) list the sequence of the tags / values that triggers the alarm too. The basic steps to use a ProDiag with an HMI are explained in the SIOS Forum at https://support.industry.siemens.com/tf/us/en/posts/155719/ Here there are the configuration main steps related just to adding the criteria analysis in the attached ProDiag sample program: PLC Side:
HMI Side: