Hello, I have the same exact problem: the SetBitWhileKeyPressed function get stuck after the button is no longer pressed. I am on TIA V16 Update 5. The issue happens rarely, but it does, and it would damage the machine. Also, we cannot afford to stop the machine with the emergency every time this happens. Might the communication channel be overloaded? Or else? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 09/15/2022 04:27:53New subject after splitting |
|
9/15/2022 4:38 AM | |
Joined: 12/18/2014 Last visit: 9/25/2024 Posts: 33837 Rating: (4205) |
Install the Update 6 for TIA V16. Maybe it helps. Updates for STEP 7 V16, S7-PLCSIM V16 and WinCC V16 |
9/16/2022 1:13 PM | |
Joined: 8/3/2009 Last visit: 9/25/2024 Posts: 13788 Rating: (1741)
|
Hello It depends also which type of PLC you use. for example a S71200/1500 has a compleate different timing in HMI communication than a S7300 for example. in the new PLcs the HMI Communikation is a compleatly parallel task. (for example: LINK) this could lead to the mentioned behaviour if you for example use In/out parameters or FBs. this could lead to overwrite problems. -> LINK Bye Murof |