1/15/2020 7:49 PM | |
Posts: 162 Rating: (8) |
Couldn't it be a problem of library ? Are the faceplates you are using in your screens also well pushed to the multi user project ? |
1/16/2020 9:52 AM | |
Joined: 8/3/2009 Last visit: 5/6/2024 Posts: 12884 Rating: (1645)
|
Hello Divej93 First we need to know do you have WinCC Comfort/Advanced or a WinCC Professional RT Project? - For WinCC Prof look at this LINK - for WinCC Basic/Comfort/Advanced its quite the same. If you add a Graphic the Graphic has to be added in the Graphic Library of the Project. This global Informations you cannot use with Multiuser Server. So if you want to Check in only the Screen change will be checked in and the new Graphic in the Library will not be checked in (because ist not supportet). -->> So If you want to Add new Graphics in the Project do this in the Server View/Session! Bye Murof |
If this Information really helps, you could use the Rate function |
|
1/20/2020 2:56 PM | |
Joined: 9/17/2015 Last visit: 10/4/2023 Posts: 137 Rating: (4) |
Hie Murof, Thanks a lot The Solution works. |