10/23/2019 6:42 PM | |
Posts: 152 Rating: (5) |
|
10/23/2019 6:42 PM | |
Posts: 152 Rating: (5) |
|
10/23/2019 7:00 PM | |
Joined: 9/16/2013 Last visit: 1/5/2024 Posts: 511 Rating: (105) |
This should be enough what you choised on 2.png, just to select HMI as a slave in time synchronization. Take a look page 25 inside document https://support.industry.siemens.com/cs/attachments/69864408/69864408_TimeSynchronization_en.pdf There is also option that Inside DB PLC stores time and HMI read that, but this is not necesary. |
Last edited by: SOble at: 10/23/2019 19:00:58Last edited by: SOble at: 10/23/2019 19:02:04Website: |
|
10/25/2019 12:15 PM | |
Joined: 8/3/2009 Last visit: 4/30/2024 Posts: 12869 Rating: (1642)
|
Hello You also have to be sure that if you use the Slave Time Synchronisatoin that the System Time of the PLC will be used for the synchronisatoin -> So you have to use the same Timezone and Daylight Safing Time Settings on Comfort Panel -> Be also sure that the TP1500 Comfort cannot change automatically the Daylight saving time -> You have to use this one for example: https://support.industry.siemens.com/cs/de/en/view/109482675 in which coutry do you work? do you have daylight saving Time? Bye Murof |
If this Information really helps, you could use the Rate function |
|