11/29/2014 2:53 PM | |
Posts: 14 Rating: (0) |
hello I have problems with values, i want to have a possible to change values in wincc for example, time or counter values. With real(analog) values I dont have problems, I have just with time and counter blocks. See on the screens what im doing wrong :/ There where is a red line must be some value, but i have only "Unknown" On the screens i tried to set a good data type, but im doing something wrong, does anybody have some example how to set this correct? Please help. Stuff : tia v12 KepserverEX5 WinCC 7.3 S7-1200 tcp/ip connected materials for kepserver : http://www.kepware.com/Support_Center/SupportDocuments/Help/siemens_tcpip_ethernet.pdf#page=40&zoom=auto,61.5,288.75 Attachmenttia v12 values problem.zip (145 Downloads) |
11/29/2014 4:38 PM | |
Posts: 14 Rating: (0) |
SOLVED timers have to be tag like : DB2.DBW2 counters have to be tag like DB3.DBD2 |