3/25/2013 12:55 PM | |
Joined: 9/23/2005 Last visit: 9/19/2024 Posts: 4347 Rating: (1446)
|
Hi, Despite of it is pretty simple; here there is a sample project that exemplifies the use of diagnostic memories. The project has two analogical modules, once in the central rack, the other one in the ET200MP. In the Modules Properties (Device View), I set the diagnose bit function (Module Parameters -> Value status). Optionally, I set all diagnose possibility for the first channel too (Module Parameters -> AI8->Inputs-> Channel0). The analogical values (and the diagnostic bits) could be showed at the Watch Table. An primitive example of use of the diagnostic bit is showed on the OB1. AttachmentDIAG_BitDiag.zip (651 Downloads) |
Last edited by: O_Moderator at: 3/25/2013 1:39 PMDenilson Pegaia |
|
7/24/2016 9:06 PM | |
Posts: 5225 Rating: (1192)
|
Hi Greg, Please see the attached PDF with some hints on how the configuration of the original example works. See if helps... otherwise give the guys a sample project to work from with your application problem. Cheers. AttachmentVisual clue_Diagnostic bits.pdf (430 Downloads) |
Last edited by: William_B at: 7/24/2016 9:07:28 PMattach file (oops) |
|