6/2/2021 7:54 PM | |
Joined: 9/23/2005 Last visit: 12/8/2023 Posts: 4284 Rating:
|
Hi, So, decide to write here some tips regarding this subject: Compared with V16 version, TIA V17 implement some security measurements, so it is not more possible to simulate an WinCC Unified Project using a predefined (in WinCC Unified – Configuration) Administrator user / password. So, to simulate a WinCC Unified Project it is now necessary that at least one user is predefined in the project configuration (or that the UMC server features, which is more work). Then follow the steps to configure the user:
(special thanks to Ms. Ellena Witti, for the additional TIPs) Additional TIP: In some cases it is possible to get the message "the url****/SwacLogin is unavaliable". It could be fixed in the browser settings, like descripted in TIA V17 help system, under "Information System, Visualizig process (RT Unified), Compiling and loading (RT Unified), Unified PC (RT Unified),SwacLoging: Error after compleet download. |
Last edited by: Denilson Pegaia at: 06/02/2021 20:09:06Last edited by: Denilson Pegaia at: 06/02/2021 20:10:01Denilson Pegaia |
|
This contribution was helpful to
6 thankful Users |
8/30/2021 12:19 PM | |
Joined: 9/23/2005 Last visit: 12/8/2023 Posts: 4284 Rating:
|
Hi, I suggest to
|
Denilson Pegaia |
|