Dear big_muzzy, you are right, the times in the instance-DB are not accected by the system-time. The time at the PT-input tells the block how long a rising edge at the IN-parameter should be delayed. At the ET-output you can see the time that has passes since the last rising edge at the IN-input. In the attachment you can see a detailed description from the block-help. I hope this helps. Best regards, yy1 |