1/9/2015 5:55 PM | |
Joined: 1/28/2009 Last visit: 10/26/2024 Posts: 6852 Rating: (1365) |
You can try calling the Timer in another network! Rules for branches in LAD |
Last edited by: hdhosseini at: 1/9/2015 6:03 PM |
|
5/23/2017 12:40 AM | |
Joined: 2/20/2017 Last visit: 5/18/2024 Posts: 2 Rating: (0) |
Moi aussi j ai le meme probleme avec cpu 1214 vraiment en attendre un expert de simens nous repondre |
8/31/2017 1:57 PM | |
Posts: 21 Rating: (21) |
Add a coil at the end of the Timer and problem will be solved. This is really a funny bug from TIA. |
This contribution was helpful to29 thankful Users |
12/17/2018 8:01 PM | |
Posts: 2 Rating: (0) |
Thanks. It works now :) |
This contribution was helpful to1 thankful Users |
12/29/2018 2:41 PM | |
Posts: 3 Rating: (0) |
thanks this worked for me too |
This contribution was helpful to1 thankful Users |