11/6/2019 4:21 PM | |
Posts: 22 Rating:
|
Good day, I would like to know if Sinamics S210 have torque control option available? If so, how should it be commisioned? With regards, Jurek Dudek |
11/7/2019 7:53 AM | |
Joined: 2/7/2018 Last visit: 3/14/2023 Posts: 181 Rating:
|
Hi, The SINAMICS S210 is a servo speed-controlled drive. There is no specified parameter where you can choose “torque control”, like in S120 via parameter P1300 (control mode). In fact, a SINAMICS S210 will never operate standalone and requires a SIMATIC controller (S7-1500 / S7-1500T) with motion control functions (like “PositioningAxis”). With the motion control functions, you are able to limit the actual torque. This function is called „MC_TorqueLimiting“. Further Information about the “MC_Torque” function can be found in the SIMATIC Motion Control Manual, Chapter „10.12.1 MC_TorqueLimiting“, pdf-page 471: https://support.industry.siemens.com/cs/ww/en/view/109749262 Additional we offer an application example for configuring technology objects with SIMATIC S7-1500 and SINAMICS S210 in TIA Portal: https://support.industry.siemens.com/cs/ww/en/view/109749795 Best Regards, |
This contribution was helpful to
1 thankful Users |
11/7/2019 1:45 PM | |
Posts: 22 Rating:
|
Thank you for responses. Does that mean V90 could also be set to "torque control" mode using TOs on S7-1500/S7-1500T? Woth regards, Jurek Dudek |
11/7/2019 2:55 PM | |
Joined: 2/7/2018 Last visit: 3/14/2023 Posts: 181 Rating:
|
Yes, V90 can also support “MC_TorqueLimiting”, but I would recommend to use latest Firmware of SINAMICS V90 (https://support.industry.siemens.com/cs/ww/en/view/109746210), because for extended “Torque-Commands” you might need telegram 750, which will be supported with V90 FW Version V1.03 or higher. Here you will find the requirements for “MC_TorqueLimiting”: Requirements for force/torque limiting: ● The technology object and the reference torque of the drive have been configured correctly. ● No enable-preventing errors are pending for the technology object (the technology object does not have to be enabled). ● The drive must support force/torque reduction. Only PROFIdrive drives with SIEMENS telegram 10x support force/torque limiting. ● Interconnection in the SINAMICS drive: – P1522 to a fixed value of 100% – P1523 to a fixed value of -100% (e.g. through interconnection to fixed value parameter P2902[i]). Best Regards, Technical Support for SINAMICS S210 |
Follow us on