Hello, to connect the parameters in the S120 with the telegram you can simply use the provided script. You can download it on our “SIMATIC Winder and Tension Control” Homepage:https://support.industry.siemens.com/cs/us/en/view/58565043 See Downloads -> TIA-Portal -> Script for drive configuration. A description of the interconnection is also provided within our documentation in chapter 5.5.1 LCon_DriveControl. I guess you are using the version without technology objects in the SIMATIC? The upper torque limit can also be negative it must only be always bigger than the lower one. You can also see the correct interconnection within our demo project which you can also download on our homepage. |