7/31/2015 10:44 AM | |
Joined: 10/31/2014 Last visit: 3/1/2024 Posts: 58 Rating: (5) |
hello, any one use 1 count module for totalize flow . pls suggest me. if any.. |
8/9/2015 10:10 AM | |
Posts: 8946 Rating: (999) |
Explain more clear. |
4/12/2016 1:01 PM | |
Joined: 5/28/2008 Last visit: 4/15/2024 Posts: 4505 Rating: (835) |
Dear Both. I am very sorry. I did not understand the question But In any case, I have understand that we are talking about flow totalizer. The flow transmitter give you reading to represent (Volume / Time) like cubic meters / min. The sampling time you fetch the value to calculate the totalizer is important in order to make accurite calculation. I said calculation and not only addition. Thus because time should factor of the equation and to simplify your job, you can use the premade FC from Siemens here. How can you add together physical flow measurements (mass flow rate, for example) to a total value in STEP 7 V5.x? |
Ayman Elotaify |
|
This contribution was helpful to1 thankful Users |
4/12/2016 5:59 PM | |
Joined: 7/24/2014 Last visit: 12/4/2023 Posts: 392 Rating: (66) |
Dear Ayman Here as it isclearly mentioned in the subject of the post that the flow needs to be totalize so how a time comes to the picture and second thing is that it is about the flow meter giving pulse so just adding or if its a hsc then its according to hsc programming type have to incorporate thats all Regards Smit Shah |
Thanks and Regards |
|