9/7/2018 5:21 AM | |
Joined: 7/5/2013 Last visit: 4/22/2025 Posts: 3148 Rating:
|
Hello Anshuman, is your issue about the VarValue of PT_01_PV and PT_02_PV? What do you mean with "spare value"? Which DataType are you using for the PT_xx resp. TT_xx tags? Do you have the same value when displaying the PT_xx tags in an IO field? Regards, Frink |
Pi is exactly three! |
|
9/7/2018 6:05 AM | |
Joined: 2/9/2016 Last visit: 4/13/2025 Posts: 79 Rating:
|
Mr.Frink thank you for your response. Yes, my issue is regarding the 'VarValue" of PT_01_PV and PT_02_PV. Spare value means my PT Min/ Max range are between 0 to 200. in I/O field of HMI that is showing between 0 to 200(4-20mA) this value are matching with the field transmitter. But in CSV files which we are delimiting there this are showing random values in 'VarValue" . using "Real" data type. |
Anshuman Singh |
|
9/7/2018 7:20 AM | |
Joined: 7/5/2013 Last visit: 4/22/2025 Posts: 3148 Rating:
|
Hello Anshuman, if pressure was about 1.1bar, it seems for some reason the real (resp. floating point) values are shown in integer format. Are the temperatures real values, too? Are you logging temperatures and pressures to the same archive? Can you upload such a csv file? Regards, Frink |
Pi is exactly three! |
|
9/7/2018 8:06 AM | |
Joined: 2/9/2016 Last visit: 4/13/2025 Posts: 79 Rating:
|
Hi Frink, Yes , Temperature are also in real they are also showing random values. No, data Archive for Pressure & temperatures is different. I have attached a screenshot for your reference. Thanks.
|
Anshuman Singh |
|
9/7/2018 8:08 AM | |
Joined: 2/9/2016 Last visit: 4/13/2025 Posts: 79 Rating:
|
I have attached CSV file for your reference. AttachmentTIA 14 DATALOG_CSV.xlsx (186 Downloads) |