Hello Dileee on the CF Card there are no project data, only logged data or recipe or similar (user data). So often there is an active access rto the card while runtime is running. I Would recommend stopping the Runtime and then you can safely remove the CF Card. Then you can try to restore on the other panel. A restore usually should only take a few minutes. you have to activeate the restore manually: https://support.industry.siemens.com/cs/ww/en/view/28928853 Bye Murof |