Hello Everyone I just want to share one of my recent Experience Its not related by amymeans with Siemens or automation We are having one 2MVA Transformer for PCC, and during DGA analysis of oil, we found some Gases so we took Job to find root cause We checked and found some angle and bolts were inside - But they may not created problem. Core earthing strip was not properly connected so we reconnected it back and removed foreign Material and now result is Good This is just to share. Photos are attached Regards Devesh Vithani Attachmentsnaps.zip (319 Downloads) |