I m trying to connect the OP17 with s5 100U cpu 100 and hv download a file for Coros Function Blocks I have some questions regarding this plz try to help me about. 1- First let me confirm that this file is OK for that which i hv attached below? Which of these file is for my CPU 100?? 2- Is this nesseary to use this FB51 while i just want to check communication with the OP17? 3-When i m tryingS5TD02ST.S5D my cpu going to stop mode, I have write :C DB 51 :L KF 1 :T DW 40 in OB21 and OB22. 4- l ky51,0 :JU FB 51 NAME :TDOP:511 :T FW 100 in OB1 5- DB51 with 70DW with KH 0000, for all DW 0-68 is there is some thing which i m not getting.
Attachmentop_s5.zip (474 Downloads) |
Last edited by: Min_Moderator at: 10/15/2014 1:27 PMNew subject after splitting from /tf/WW/en/Posts/64953#top Last edited by: ALI KK at: 10/15/2014 8:37 AM |
|
10/15/2014 9:39 AM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308)
|
Hello ALI KK The file S5TD02ST.S5D is the right file to be used with S5-100U 9 CPU 100 ) To Analyse the problem pl check the Error code in FW 100 and also analyse ISTACK. If required, please post the observations here for analysis. Cheers Navnag |
There is no such thing as the last bug in a program |
|
10/16/2014 10:22 AM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308)
|
Hello ALI KK The iSTACK details provided by you are not sufficient. Pl upload the Complete Istack Screenshot ( Both Pages ) here or upload your S5 program for analysis. Cheers Navnag |
There is no such thing as the last bug in a program |
|
10/17/2014 10:18 AM | |
Joined: 7/4/2011 Last visit: 9/27/2024 Posts: 35 Rating: (0) |
Here is the progrm attached below. It has only OB1,OB21,OB22,FB51,DB51 with DW70 AttachmentS5 PLC to OP project.zip (497 Downloads) |
Last edited by: ALI KK at: 10/17/2014 10:24 AMLast edited by: ALI KK at: 10/17/2014 10:23 AM |
|
10/17/2014 10:26 AM | |
Joined: 7/4/2011 Last visit: 9/27/2024 Posts: 35 Rating: (0) |
and cable which i m using through diagram attached here |
10/17/2014 8:14 PM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308)
|
Hello ALI KK Here is what I found :
The FB 51 used by you is from the file S5TD01ST.S5D ( Which is forCPU 103 and not for CPU 100. I have copied the correct FB to the file.
DB 51 in your program has only DW 0 to DW 64 ( i.e. 65 Data Words ) against 70 required. Pl find attached the modified S5 program, Hope this helps Cheers Navnag Attachment100U@@ST.zip (443 Downloads) |
There is no such thing as the last bug in a program |
|
10/21/2014 7:12 AM | |
Joined: 7/4/2011 Last visit: 9/27/2024 Posts: 35 Rating: (0) |
Sorry but the status of the PLC is same as before even downloaded your updated program but not sucess. Cpu is still in Stop mode when ever i try to download this FB51. Here is the file for Istack and Bstack of my 100U 100 cpu. SECONDLY: I have also a 95u cpu and i downloaded a progrm from my machine which have a 95u in running condition i downloaded same blocks just for communication testing like OB1,OB21,OB22,FB51and DB51 with dw69 length. Plz can you give me OP block file for different CPU (Coros Standard Function Blocks) for 100u CPU100 Thnks Regards
AttachmentIstack,Bstack.zip (395 Downloads) |