8/10/2016 3:06 PM | |
Joined: 4/13/2012 Last visit: 2/25/2025 Posts: 29 Rating:
|
Hello, I wanna send some simple data from 1 to for now second PLC, and later will add more PLC's to them I am new into the TSEND etc, and have attached a simple start with 2 x 1214C first one is a 40 the second 31. I have this working with a PUT instruction, but what am I missing here?? Thanks! Jeroen Attachmentmeteoserver1.zip (39 Downloads) |
8/10/2016 3:45 PM | |
Joined: 7/9/2015 Last visit: 3/27/2025 Posts: 4210 Rating:
|
Hi, I have seen several things: TRCV_C should be enabled with "true" and not with 10Hz clock... Did you check the Error and Status outputs ? If Error ist true, then save Status. I am not sure but you only send one bit?! First check Status, then we will find out your problem. Please check this FAQ: How do you program the TSEND_C and TRCV_C instructions for open user communication over the integrated PROFINET interface of the S7-1200 CPU?Regards, Towome |
Last edited by: Towome at: 8/10/2016 3:48:16 PM
|
|
8/10/2016 4:39 PM | |
Joined: 4/13/2012 Last visit: 2/25/2025 Posts: 29 Rating:
|
I have changed LEN to 0 and now it is working!!! Thanks!! Jeroen |