Hello, I would check the EMC guidlines first: http://support.automation.siemens.com/WW/view/de/60612658/0/en With service access level you can trace the sin / cos encoder tracks (see parameter p496 ... r499) - trigger event "error active" / trace within current controller cycle at low speed. Maybeit isalways on the same mechanic position area - than you should check the encoder mounting. Regards Zako |
Last edited by: zako_ at: 2/2/2013 10:50 PM |
|
4/23/2014 5:42 PM | |
Posts: 1 Rating: (0) |
hi vadak i have same problem can you tell me how you fixed it please
|