Check the IP address it should be for S7-300 192.168.0.1 and S7-400 192.168.0.2 for example |
Warm Regards |
|
1/25/2016 10:09 AM | |
Joined: 7/9/2015 Last visit: 3/14/2025 Posts: 4198 Rating:
|
Hi,
I think your Router blocks data. Port 102 ist blocked by default i.E. and must be enabled for complete transfer route. Please have a look to FAQ: Which ports are used by the various services for data transfer by means of TCP and UDP and what should you watch out for when using routers and firewalls? https://support.industry.siemens.com/cs/ww/en/view/8970169
Regards, Towome |
|
|
1/25/2016 10:34 AM | |
Joined: 5/12/2006 Last visit: 3/14/2025 Posts: 22588 Rating:
|
Hi, but he can connect the S7-317 with the same router/switch HW , so the problem should not a blocked Port or? I think the IP Configuration of the CP400 is not the same like the S7-317. There is a option "Use Gateway" in the IP adress settings of the CP/PLC, and here must be configured the right addresses.
Christoph |
1/28/2016 11:59 AM | |
Posts: 9 Rating:
|
Even if I have done setting of router ip address in CP card , still PLC not accessible, even ip 10.112.123.83 is unreachable |
1/29/2016 10:30 AM | |
Posts: 9 Rating:
|
Ok. Let me try. I have downloaded to CP card ,not to the PLC. |
2/3/2016 9:42 AM | |
Posts: 9 Rating:
|
Hello, I downloaded to CPU thorugh netpro. Its working ,Thank u very much for suggestion. |