2/7/2011 12:19 AM | |
Posts: 23 Rating:
|
Dear Experts, I programmed by following CP-ptp samples by using FB2, FB3 (P_SEND, P_RCV). but i got a message "unable to copy FB2, FB3" while downloading and CPU SF light coming and goes to stop. But i can simulate with PLC SIM no problem at all. So kindly advise me the way to solve my problems. I am using CP340 in ASCII mode to test hyperterminal. Thanks in advance! Bgrds, Phyoe AttachmentFB3 from CP ptp library.pdf (192 Downloads) |
2/7/2011 9:31 AM | |
Joined: 10/7/2005 Last visit: 3/25/2025 Posts: 3042 Rating:
|
Hello phyoemaung What is the part number of your CPU, how old is it? Gut feeling tells me it is an ancientone which does NOT have SFB52/53 in it (these are called inside FB2&FB3) and that's why it does not allow the download. The easiest way to to findout which SFC's and SFB's your CPU support please isthis: 1.) Connect to it, select the CPU or blocks folder andgo to Module information (CTRL+D) 2.) Go to the "Performance Data" tab and see what System Funtions are in your CPU. If SFB52/53 areNOT listed, you can NOT use FB2&FB3 (P_SEND, P_RCV) and instead need to use "P_SEND_OLD" and "P_RCV_OLD" (these use SFC58/59 instead and canbe found in the same CP340library as FB2/3). I hope this helps |
Cheers |
|