4/3/2023 6:40 AM | |
Joined: 4/28/2009 Last visit: 12/8/2023 Posts: 286 Rating:
|
Hello, for start the drive you need also rising edge on ON/OFF1 signal. You selected macro 41 which predefine analog input as source for requested speed, DI0 as command for start and DI5 as command for acknowledge fault. So if analogue input is working you have to only activate 24V on DI0 and drive should run. If you still can't run the drive, check selecting ON /OFF function setting. You can have switched selection to another command (OFF1) than macro preselect (OFF2). This settings is described in operating manual in chapter Advanced commisioning - Selecting the ON/OFF functions. With regards Martin |