10/7/2016 1:06 PM | |
Joined: 4/28/2015 Last visit: 11/19/2024 Posts: 7 Rating: (0) |
HELLO , I NEED A help for wp321 with tia portal v13 update 9..i have a under voltage error in my program. i am useing a third party 4 wire load cell..waight load range is 150 kg to 1000kg ..how can i solve this problem .. ------------------------------------------------------------------------------------------ |
Last edited by: AutoGen_948162 at: 10/7/2016 1:09:35 PMLast edited by: Min_Moderator at: 10/10/2016 1:25:13 PMNew subject after splitting |
|
10/11/2016 10:15 AM | |
Posts: 206 Rating: (22) |
Hello, your problem is that the tension on the SENSE terminals of the WP321 is to low. If you have a 4 wire load cell you have to make two bridges, one between Exc+ and Sen+ and one between Exc- and Sen-. See also the manual chapter 6.2 image 6-2 https://support.industry.siemens.com/cs/ww/en/view/109738535 If you have already made the bridges there might be a wire break in the Exc or Sen wires. Regards ABenno |
10/12/2016 7:49 AM | |
Joined: 4/28/2015 Last visit: 11/19/2024 Posts: 7 Rating: (0) |
thanks for that... now i have a problem again ..i confused in parameters which data records (DR) and command i can useing with load cell..and how can i use it in my program ... ? if load cell Norminal output- 3.0 mv/v excitation voltage-10V DC -Maximum 15 vdc LIFEBIT OF FB WP321 is fleshing on/off ...continuously
Attachment5920210 - pdf.pdf (312 Downloads) |
Last edited by: AutoGen_948162 at: 10/12/2016 9:01:31 AM |
|
10/17/2016 11:16 AM | |
Joined: 1/4/2007 Last visit: 12/2/2024 Posts: 1152 Rating: (175)
|
Hello AutoGen, There exist no parameter in the WP321 module for the Nominal Output. You can connect load cells with a Nominal Outputup up to 4 mV/V.
|