Hi Maikol89, What role is the user assigned to? In the case of "HMI Monitor Client", the user is not allowed to write PLC tags. Kind regards |
9/4/2023 6:32 AM | |
Joined: 7/24/2023 Last visit: 2/13/2025 Posts: 41 Rating:
|
Hi Stefan, thank you for your help, I solved the issue. The mistake was that on the user administration there was flags on all roles for my user, including "HMI Monitor Client" role (see attachment). This is a mistake because, as I can see from "HMI Monitor Client", " The "HMI Monitor Client" HMI role is superior to all other roles and their function rights. A user who is assigned the "HMI Monitor Client" role is only granted the functional rights of this role. Function rights with a higher precedence, of other roles that are assigned to the user, are lost. " Thank you again for your support. Best regards, Maikol |