Hello Jota.Catrileo well, the 331-7KF01 is rather ancient, but here afew ideas from my side anyhow: 1.) Leave the configuration as 7KF02 and simply plug in the 7KF01 andchances are it willwork(the 7KF02 is meant to be "functionally identical and fully compatible"with 7KF01, see also HERE for more). 2.) In case7KF01is located in an ET200M: Grab the GSD file forthe ET200M and configure it GSD file based with a 7KF01 instead of using TIA portal HW catalogue metadata. 3.) If all fails, get an emergency delivery for a 7KF02 (I'd rather do that than contemplating manually rewritingthe TIA Portal Step7 program with Step 7 "classic). I hope this helps |