5/19/2017 10:51 PM | |
Joined: 4/27/2015 Last visit: 5/22/2024 Posts: 7 Rating: (0) |
Hi dear freinds. I tried to connect turbidity meter Turbimax CUE21 to SM1231 AI module. Turbimax has Analog output 4-20mA:
The issue is that the value is unstable. %IW of analog input randomly changes from correct value to maximum. The value on the Turbimax display not changes. The current in circuit is stable 5.7mA. Why the value skips, when current of input stable? |
Last edited by: barsice at: 5/19/2017 10:52:10 PM |
|
5/19/2017 10:56 PM | |
Joined: 2/2/2015 Last visit: 8/25/2024 Posts: 124 Rating: (21) |
Hi barsice, What's you CPU type ? You may need to make a grounding for PLC and Analog Input SM card. Regards; Ahmed Kadry |
5/21/2017 12:43 AM | |
Joined: 4/27/2015 Last visit: 5/22/2024 Posts: 7 Rating: (0) |
Yes. To this Analog module connected other sensors (level, pressure), and it work properly. |
5/21/2017 1:41 PM | |
Posts: 102 Rating: (10) |
for faster help, send a screenshot from program and wiring please |
5/22/2017 12:08 PM | |
Joined: 2/2/2015 Last visit: 8/25/2024 Posts: 124 Rating: (21) |
Hi barsice, Your answers in points (1 , 3) makes us sure that the faulty comes from Turbidity sensor noise so I suggests point 2 to be the accurate solution in order to eliminate the noise from the sensor itself. In the sensor side you have connected a shielded cable (one terminal to +ve, one to -ve and the shield to GND pin ) Right ? My suggestion is in the PLC side to connect ( +ve cable terminal to +ve analog input pin ) , ( -ve cable terminal to -ve analog input pin and chassis GND ) , ( Shielded terminal to chassis GND ). By this way we try to make a noise filter. (This way is a completely hardware) Regarding software, please read this Topic , refer to huggy_d1 reply. any updates will be appreciated, Hoping to solve your issue. Regards; Ahmed Kadry |
5/22/2017 2:48 PM | |
Joined: 4/27/2015 Last visit: 5/22/2024 Posts: 7 Rating: (0) |
Yes. It was first initial scheme of project. Of course I tried this connection. Thank you for topic. It's same problems, and same connection of sensors. But I always ground all chassis and ground pins all modules. But M pins and 0V of source I don't ground. Is it mistake? |
5/22/2017 3:55 PM | |
Joined: 2/2/2015 Last visit: 8/25/2024 Posts: 124 Rating: (21) |
You could try and then we could make sure after this, as I haven't grounded them ever so I couldn't expect the behavior of signal after this solution But surely I hope to get the right solution for your mistake, and Please don't forget the site feedback. Regards; Ahmed Kadry |
This contribution was helpful to1 thankful Users |
5/23/2017 8:36 AM | |
Joined: 4/27/2015 Last visit: 5/22/2024 Posts: 7 Rating: (0) |
Of course it is not wired as drawing. It is mistake of projects. I've attached correct scheme. |
11/12/2018 10:00 PM | |
Joined: 12/1/2015 Last visit: 8/23/2024 Posts: 1 Rating: (0) |
I had the same problem and when I jump the wire in GND and A + or A- the signal stabilizes, thk !! |