Hi, I'm sorry to say, that you will have no chance, to save your project. An OP15 will not supported by ProSave, and therefor you have to use an identical target panel with the same part number: https://support.industry.siemens.com/cs/ww/en/view/11017496 If you would have the project, you could migrate a COMTEXT project into a ProTool project: https://support.industry.siemens.com/cs/ww/en/view/23212529 COMTEXT and ProTool projects are incompatible and both tools are out of date and not available any more. So my suggestion is: Make a complete new project with an actual software tool like TIA Portal. |