8/1/2019 5:51 PM | |
Posts: 111 Rating: (31) |
Hopefully unrelated, but.
The old teaching was to never connect switch-mode power supply (PSU) together. Reason: The PSU measures its own output to regulate and also protect against short-circuit. The switching frequency generated by a "foreign" partner PSU can interfere with the measure process. Occasionally the PSUs can fight each other for dominance pushing the voltage too low. Probably newer PSUs can handle it, though it will be nice if some specification sheet would say that parallel connection is possible. No all device ranges (even in the same brand) is created equal. Additionally the following link suggests how redundant connection should be done - https://www.deltapsu.com/technical-articles/how-to-operate-parallel-and-series-connection Check for badly fastened wires or wires with bad connectors. (remembering experience of loose connector that gave problems 4 months after commissioning, which was not operator sabotage) |
Last edited by: AutoGen_1801304 at: 08/01/2019 17:56:47// sorry huggy_d1, did not mean to repeat what you said. |
|
8/1/2019 7:26 PM | |
Joined: 2/28/2017 Last visit: 8/10/2023 Posts: 8 Rating: (1) |
I did check the tech specs before selecting this model. It does explicitly state that these may be paralleled. Very informative link. We're also using double-conversion UPSs. They have the inverter always online so that there is no switch-over delay and it actively regulates the output. They also have a network management card which reports events to a central syslog server, as well as having internal web page with event log. |