You can send your project via email https://support.industry.siemens.com/cs/us/en/view/109740696 |
Last edited by: Jen_Moderator at: 06/07/2022 11:26:55Link optimized. - Trying is the first step towards failure. |
|
This contribution was helpful to
1 thankful Users |
6/14/2022 9:19 AM | |
Joined: 7/1/2014 Last visit: 4/17/2025 Posts: 236 Rating:
|
That's how i solved it. Thank You. |
This contribution was helpful to
1 thankful Users |
12/16/2022 9:00 AM | |
Joined: 10/25/2022 Last visit: 4/11/2025 Posts: 3 Rating:
|
Am I missing something or there is no information on how the issue was resolved. I hope you share this with us because the same thing happened to me today. |
12/16/2022 3:56 PM | |
Joined: 3/5/2017 Last visit: 4/15/2025 Posts: 780 Rating:
|
You need to reload the project, to restore original users. Unless you have backup file. What the emailing solves is that you do not have to use engineering tool to do that. You can load project to your PC and then send it on site with e.g. e-mail. EDIT: There has been a lot of issues with password aging, when you test your configuration lets say on FAT, everything works fine. But when the product is installed on customers site, that may take months, passwords have aged and no one can log in anymore. Program should ask you to change aged password, but for some reason this does not happen all the time. I have begun to create users for the customer which have only user administration rights, whos password will never expire.
|
Last edited by: K_Ohjus at: 12/16/2022 16:05:45- Trying is the first step towards failure. |
|