4/2/2013 9:28 AM | |
Joined: 10/7/2005 Last visit: 10/5/2024 Posts: 3024 Rating: (1054)
|
Hello Haz3y14 Good news first: Yes, it is absolutely possible to use a DP/DP coupler for Profibus DP based S5 IM308C <-> S7data exchange (done it many many times myself). The devil is in the detail though when it comes to the IM308C configuration and S5 I/O addressing(linear P or Q area based addressing orpage addressing orFB192 usage, DB1 usage/setupetc.)and I urge you to start by having a good read of the ET 200 Distributed I/O System with IM 308-C and S5-95U manual, especially chapter 6.1. Theother manual of interest is of course COM Profibus and Ihope this helpsto get you started. |
Cheers |
|
4/2/2013 9:33 AM | |
Joined: 2/12/2013 Last visit: 8/9/2024 Posts: 4 Rating: (0) |
Hey fritz, Thanks for the manuals! I need all the help I can get with S5! |
This contribution was helpful to1 thankful Users |