12/15/2010 7:21 AM | |
Joined: 8/10/2006 Last visit: 2/13/2025 Posts: 156 Rating:
|
Hi, Using FC16 I am unable to write registers in MB slave. I am always getting error code 0E47 or 0E40 on master CP. Can you please help. Please note that I am using two CP341-422 RTU as master and slave. Regards, Raheel Splitted from Modbus Master communication. |
Last edited by: O_Moderator at: 12/16/2010 11:22 AMnew subject after splitting |
|
12/15/2010 12:19 PM | |
Joined: 8/10/2006 Last visit: 2/13/2025 Posts: 156 Rating:
|
Hello, Below please find my configuration. please note that 0E47 message is on modbus master. Regards, Raheel AttachmentMB Config.zip (170 Downloads) |
12/16/2010 3:01 PM | |
Joined: 8/10/2006 Last visit: 2/13/2025 Posts: 156 Rating:
|
OK Thanks. Will try this on Monday and let you know Regards, Raheel |
12/21/2010 6:54 AM | |
Joined: 8/10/2006 Last visit: 2/13/2025 Posts: 156 Rating:
|
Hi, By changing the LEN parameter it worked in first time. Thanks for all your support. Best regards, Raheel |