hi Thommy4life, You can´t see the pulses on one of these addresses. Counter-modules are used because the signal is faster then the CPU-cycle. So they are counting the incoming signals. What you can find is a counting-value or a measuring-value, or both. Have a look in the manual of the counter-module, chapter4. SIMATIC ET 200SP TM Count 1x24V When you are projecting the counter with a Technology-Object(TO), the TO is getting the data out of the address-space and is preparing the data for you. When you work without TO you have to use the control- and feedback-interface, which you can find in Chapter 4.3.5. In the feedback-interface you will find the Counter-values and measured-values. hope this helps, regards, |