Sir, |
12/11/2014 5:17 PM | |
Posts: 87 Rating:
|
Hi. Maybe you can configure a DI for OFF3. For example we can use DI1 for OFF3. You must do this: p848[0] = r722.1 p848[0] = Parameter for OFF3. r722.1 = Digital Input DI1 status. Hope this helps. Regards.
|