Hello StudentIntern; Sorry, but your nickname compels me to tell you that you have a bit more studying to do for this project,. The DPV1 Read/Write functions for S7-300 and S7-400 are SFB 52 and SFB 53; I have printed out the descripion of these function blocks from the System and Standard functions manual, you can look at it through this link: System Software for S7-300 and S7-400 System and Standard Functions Here a dwe more links, to FAQs and Application Examples, on DPV1 communications with S7 PLCs: specify the slot number in SFB52, SFB53 Last but not least, here is a manual from GE showing how to communicate to AF-650 drives over Profibus-DP. You should especially look at the chapters on parameter read/write over DPV1. You willl notice that the first infformation requested is the "slot" number; that is why I added the first link above. Note that you also have sample programs using DPV1 with Siemens drives (sorr, no GE samples...) AF-650 GP/AF-600 FP Profibus DP Operating Instructions So get ready to study and practice; you should have most of what is required for this project. Keep us appraised on how it goes, and comeback if you have any more questions. Hope thius helps, Daniel Chartier AttachmentSFB 52_53 DPV1 functions.pdf (412 Downloads) |