11/2/2021 6:38 PM | |
Joined: 3/30/2020 Last visit: 9/20/2024 Posts: 4777 Rating: (981) |
Hello. Seeing that it is an academic exercise A Guide to Fire Alarm Basics – Initiation Current Sensing Techniques using Different Current Sensors Look at the image under the heading "Ionization smoke detectors" of the first web link. This represents what you are aiming for, where the meter represents the PLC. Here the current is measured, but the PLC only has analog voltage measurement. Take note on where the meter is placed. In the old days we only had dial type voltmeters. We had to build circuits to make those meters do measurements beyond measuring volts. The easiest for your case is to add to your circuit a current sensing resistor, also called a shunt resistor. The PLC will measure the voltage on the shunt resistor which would be an indication of the current flow. Be sure to apply some math on what the size of the resistor should be. Be watchful for specifying a high enough wattage! else the resistor will burn out. The PLC has a 10bit voltage measurement which will give you an indication of how sensitive you can make the circuit. You do not have to aim for measuring the full 0 to 10V measurement range. I leave this discussion vague enough for you to figure out some details. SIDE NOTE 1 Are these notes of help? |
Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
This contribution was helpful to1 thankful Users |