Hi, i've just installed Tia 17 upd4 and the "109746530_Unified_Comfort_Panel_Images_V17_0_Upd_4.exe" When i try to change panel version on my project i can choose between 17.0.0.0 and 17.0.0.1 why?? thanks |
Did i help you? |
|
6/17/2022 1:19 PM | |
Joined: 6/19/2019 Last visit: 4/25/2025 Posts: 721 Rating:
|
Hello, And what you think version must be after instal? see improvements in update 4 and you will see what it give page 27. link HERE |
Last edited by: Mr.V at: 06/17/2022 13:24:03 |
|
6/19/2022 4:09 AM | |
Joined: 11/4/2021 Last visit: 4/19/2024 Posts: 64 Rating:
|
Hi, I noticed the same, the response from Siemens when I raised a support request was as follows:
So you can only ever select V17.0.0.1 for the HMI in TIA Portal but if you update the physical panels firmware either via USB or OTA it will be V17.0.0.4. This means that when you download to the HMI you get a warning that the versions are mismatching but apparently it doesn't matter. Just confusing. As a result of my support request an 'Important Note' was added next to the Update 4 panel image on the following page: https://support.industry.siemens.com/cs/document/109746530/image-downloads-for-hmi-operator-panels?dti=0&lc=en-NO Document attached for convenience. Attachment109746530_Unified_Comfort_Panel_Images_V17_0_Upd_4_Readme.pdf (413 Downloads) |