Hello all, I am communicating S7-1200 & V20 using MODBUS communication, while doing so can i use digital o/ps to get drive ready feedback? help me......
|
6/13/2013 5:00 PM | |
Joined: 10/11/2006 Last visit: 12/12/2024 Posts: 5969 Rating: (820)
|
Hello, the dig. output p0731/0732can be connected to any bit ofr0052/0053, even at MODBUS communication. Please find in the manual the example of the connection macro eleven in the V20s manual. http://support.automation.siemens.com/WW/view/en/67267484 |