Hello everyone. I am with this problem since yesterday and i am tearing my head off with this problem. Its my first time setting modbus with v20 inv. The cpu is a S7-1200 with a cm1241 rs485 board. I have searched through all the forum, and downloaded all the siemens modbus examples (https://support.industry.siemens.com/cs/ww/en/view/63696870) and read through all the inverter and plc documentation with no luck, appearently i am the only one having this problem. There was another guy but he solved it using DI as command source. I dont want that, i want tu run it only by modbus. So the problem is the next one: I can reach the inverter, it shows the setpoint on the BOP but it flashes between current setpoint and 0hz. If i send ON/OFF1 command to inverter it runs but with 0hz frequency, as it another source setpoint was selected. P700 and P1000 setting is 5. i have factory resetted the vfd and tried cn011, i also tried to put settings manually, and always getting the same result. r0967 shows 44e when ON/OFF1 is 0 and 044f when bit 0 is ON. Parameters P1074 shows 2018.1 as main setpoint. There is a Parameter which i cannot access (P0719) which is supossed to have priority over p0700 and p1000, but i don't know why i cannot access it from the BOP (of course user access setting is 3) which was my last option to check. Regards Edit: attached video to explain sittuation. As you can see, setpoint reaches destination, and ON/OFF1 command turns on VFD, but with 0hz setpoint. No speed from motor
|