Hi My case i am using sinamic v90 servo 6SL3210- 5FE1-5UF0 communicate s7-200Smart plc using Profinet Communication i am facing issue A07487 alarm when I give servo enable signale. But motor Running fine. Jog mode and Auto mode. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/21/2023 12:16:37New subject after splitting |
|
3/21/2023 12:49 PM | |
Joined: 12/16/2021 Last visit: 8/22/2023 Posts: 126 Rating: (2) |
Hi Vijay_Matrix, For A 07487 alarm , Connect a 1 signal to the binector input "do not reject traversing task/reject traversing task" and restart motion. Thanks
|
If The Information Helpful, Then Don't Forget Give (To thank ) and Rate It |
|
3/24/2023 2:23 PM | |
Posts: 3 Rating: (0) |
Dear Mr jack. Kindly update which parameters I have to set 1.kindly update if u have any screen shot |
3/25/2023 3:42 AM | |
Posts: 3 Rating: (0) |
I am using profinet protocol with siemens standard telegram 111 |
3/27/2023 12:02 PM | |
Joined: 12/16/2021 Last visit: 8/22/2023 Posts: 126 Rating: (2) |
Hi vijay Binector input - refer manual and download from here
|
Last edited by: Jen_Moderator at: 03/28/2023 08:33:57Link optimized. If The Information Helpful, Then Don't Forget Give (To thank ) and Rate It |
|