7/3/2019 3:31 PM | |
Joined: 4/28/2015 Last visit: 10/22/2024 Posts: 1278 Rating: (300) |
Hi, I guess you have selected the "automatic read out" function for the encoder data exchange at the Technology Object configuration. Due to the fault with "adaption…" I think there is a fault when the PLC tries to read out the encoder data. And due to false encoder data (increments per revolution) the axis goes to fast. https://support.industry.siemens.com/cs/ww/en/view/109747183 This should help |
Best regards, |
|
This contribution was helpful to1 thankful Users |
7/3/2019 5:48 PM | |
Joined: 11/17/2016 Last visit: 6/28/2023 Posts: 4 Rating: (1) |
Indeed, that's what I have done. Thank you for your advise, I will try it tomorrow ! Best regards, Jim |
Follow us on