1/16/2006 12:24 PM | |
Joined: 8/25/2005 Last visit: 9/26/2023 Posts: 1161 Rating:
|
Hello szandor, The configuration can be made in the hardware configuration. Under the options of the moduls you can define it. Have a look to the manual Programmable Logic Controllers S7-300 Module Data There you will find informations about possible values for different moduls. via PROFIBUS:
Sabine |
5/31/2011 1:00 PM | |
Posts: 691 Rating:
|
Dear saeed I think there no any way to work with Profibus, as the Communication halts when CPU goes to STOP. If you want to achieve your goal then you have to configure your Drive to Hardware level. If your Drive supports external triggering( like Siemens Drives) i.e inputs dedicated to the Drive and if you can assign some setpoints when that Input is high some internal setpoints get activated. |