Industry Online Support
Technical Forum
7/9/2012 11:05 AM | |
Posts: 18 Rating:
Hi Ajay, Thank you for your info that you are sure CU310 DP can meet my application. best regards, beard |
7/11/2012 5:44 AM | |
Posts: 18 Rating:
Dear all May this info useful for others. I got short explanation but very useful for me from Siemens AG's Engineer: Dear Mr. Mochtar, CU310 with sensorless vector control- > YES, possible, do the commissioning via Starter or Scout, you need to have vector axis, NOT servo axis. Check with parameter p1300 =20 sensorless. If you have servo mode in the axis, then you need to delete axis and repeat commissioning with vector control. Please measure cable resistance and put in p352. Take a look in description , commissioning manual chap 2.6 and function manual, chapt 4.1 Download from Internet: http://support.automation.siemens.com/WW/view/en/21901735/133300 best regards beard |
Follow us on