10/13/2013 11:41 PM | |
Joined: 10/13/2013 Last visit: 10/7/2023 Posts: 12 Rating: (0) |
Dear, I need to verify the wiring of 6ES7321-1BL00-0AA0 6ES7322-1HH01-0AA0 6ES7331-7KF02-0AB0 I have prepared wiring diagrams for these above modules. Please find attached wiring diagram and suggest any correction in it. AttachmentWiring diagram.pdf (258 Downloads) |
10/14/2013 8:49 AM | |
Joined: 1/28/2012 Last visit: 9/15/2023 Posts: 519 Rating: (83) |
Wiring for DO Module seems wrong. . Please refer attachment. . Attachment322-1HH01.pdf (168 Downloads) |
Regards, |
|
10/14/2013 12:05 PM | |
Joined: 4/19/2008 Last visit: 2/9/2024 Posts: 1525 Rating: (159) |
Hello Goldig Khan, Here is the Manual for the S7-300 Module in that you will find all the Module Detail with Wiring Connection Example. |
Ammy |
|
10/14/2013 12:20 PM | |
Joined: 4/22/2010 Last visit: 2/15/2024 Posts: 5697 Rating: (711)
|
Hello, In my opinion you should not put all connections in one drawing. To mutch crossing lines makes it hard to read. Split 1 drawing in 2 or more pages. Attached example shows what i mean. Regards, Attachmentexampleio.pdf (161 Downloads) |
Problem solved? |
|
10/14/2013 6:32 PM | |
Joined: 10/13/2013 Last visit: 10/7/2023 Posts: 12 Rating: (0) |
Dear Pranav, Are you sure that terminal 10will be connected to 0 Volt? Please find attached the reference diagram which suggesting different. Thanks Regards, Goldig Khan AttachmentDO 1HH01.pdf (152 Downloads) |
10/15/2013 6:45 AM | |
Joined: 1/28/2012 Last visit: 9/15/2023 Posts: 519 Rating: (83) |
Sorry to misguide you. . You are right. .10 should be 0V. . |
Regards, |
|