1/28/2013 4:41 PM | |
Joined: 10/11/2006 Last visit: 1/22/2025 Posts: 5985 Rating: (824)
|
Hello, I assume, that you are using a PM240, together with a CU240-S (v3.2), which has an encoder evaluation. The drive is able to run in torque control (p1300=23) while a encoder is mounted at the motor. Please find the link to the manual: http://support.automation.siemens.com/WW/view/en/27069930 |
With best regards, |
|
1/31/2013 3:27 PM | |
Joined: 10/23/2009 Last visit: 10/3/2024 Posts: 115 Rating: (0) |
Hello TechTeam, I´m using: - Sinamics G120S, (not CU320). - PM240 75 Kw. - Motor 52Kw 1LA5232. - Encoder. Greetings!
|
2/4/2013 12:38 PM | |
Joined: 10/11/2006 Last visit: 1/22/2025 Posts: 5985 Rating: (824)
|
Hello, as you listed in the post, you can run the drive in closed loop speed control (p1300=21) or in torque control mode (p1300=23). Both are vector control modes. I assume that you mean with vector torque the torque control mode. Alternatively the mode can be changed via p1501 from closed loop speed control into torque control mode. (Master slave mode). Please find the parametermanual with the function diagrams: http://support.automation.siemens.com/WW/view/en/32465038 |
With best regards, |
|